jgswartout(at)earthlink.n Guest
Posted: Fri Sep 22, 2006 1:44 pm Post subject: Eeeeek! Another fear and question. |
Bob, your 9/13/06 post regarding LEDs says in part:
Finally, relays are rated amongst the least reliable of
components. It behooves us to limit their use where ever practical.
Okay. That brings up a question. I’m planning Z13/8 with Z32. Z32 Heavy Duty E-Bus Feed shows the use of a relay to energize the alternate feed path. But Z13/8 also relies on a relay to supply the SD-8’s output to the E-Bus. That’s two relays that must work for E-Bus operations independent of battery power. Is there a practical way to avoid the built-in weakness of two relays in the E-Bus circuit?
mprather(at)spro.net Guest
Posted: Fri Sep 22, 2006 3:32 pm Post subject: Eeeeek! Another fear and question. |
A couple of thoughts...
- Relays in some applications are less reliable than some solid state
equivalents in that application. Saying hard/fast that relays are less
reliable is probably not completely accurate.
- When relays fail, often it's by degraded performance.. You'll notice
that once in a while a relay will fail to snap in, or disconnect. You
exercise the controlling switch a time or two, and it starts to function.
You make the mental note "Hmmm, that xyz relay is getting flakey; better
check it out when I get back to the hangar." And you go on with your
flight.
- The chances of a having a particular, properly installed/applied relay
failing on any flight might be 1/10,000. The chances of having two
different similar relays fail on the same flight might be 1/10,000 *
1/10,000. A very unlikely possibility.
Matt-
| Quote: | Bob, your 9/13/06 post regarding LEDs says in part:
Okay. That brings up a question. I'm planning Z13/8 with Z32. Z32 Heavy
path. But Z13/8 also relies on a relay to supply the SD-8's output to the
E-Bus. That's two relays that must work for E-Bus operations independent
of
Posted: Fri Sep 22, 2006 7:18 pm Post subject: Eeeeek! Another fear and question. |
I *assume* that while relays may be the "least reliable" of components, they
are still "pretty" reliable, else they would not appear in the Z-drawings.
But my point is that when you combine Z13/8 and Z32, the chances of the
E-bus not working in a main-alternator-failure situation are not your
hypothetical 1/10,000 * 1/10,000, rather they are increased to 1/5,000
because BOTH relays have to work, and if either one fails (1/10,000 * 2) you
are flying on the battery only, even though the SD-8 is fine. Usually Bob
endeavors to minimize the opportunities for a single component failure to
cause an emergency, and I wonder if he considers this daisy chain of "least
reliable components" in the Z13/8 + Z32 to pass muster.
N6030X(at)DaveMorris.com Guest
Posted: Fri Sep 22, 2006 7:35 pm Post subject: Eeeeek! Another fear and question. |
I think that's why it's called the Endurance Bus. So what if both
relays fail. If you've designed the system correctly, you have
sufficient battery to get to your destination, and you don't even
break a sweat.
Dave Morris
At 10:15 PM 9/22/2006, you wrote:
<jgswartout(at)earthlink.net>
Posted: Sat Sep 23, 2006 6:17 am Post subject: Eeeeek! Another fear and question. |
Well, I'm trying to understand the system I'm going to install, and some things aren't making sense to me.
Following your reasoning, since I spent big bucks on a highly reliable L40 main alternator which doesn't rely on any relay to deliver power, and on two P-mags which may not require any ship's power anyway, the highly reliable SD-8 backup alternator is just excess baggage so what difference does it make whether its electrons can get to where they are needed? That doesn't sound like correct design theory to me.
I am trying to integrate Z-13/8, Z-32, and an avionics master switch circuit of Bob’s design, and am trying to figure out where and whether to use relays which are shown in Z-32 but not in the other drawings. I note that in Z-32, the up-to-8-amp Endurance Bus feeds alternate power through a relay. (Bob has a sketch at www.aeroelectric.com/Pictures/Schematics/E-BusFatFeed.gif which says “for [E-Bus] feeds over 5A consider adding a relay to control power at the Bat Bus.”) I seem to recall that the reason for using a relay is to avoid arcing at the switch which would possibly compromise the switch.
But in Bob’s article “Avionics Master Switches: Really Necessary?,” he shows a circuit with the caption “If you really want an avionics master switch, how about doing it this way?” It shows an essential bus/avionics bus powering a transponder, turn coordinator, intercom, instrument flood, gps receiver, Nav/Comm, and fuel boost pump. Both the main feed and the alternate feed are controlled by switches, not relays. I like the idea and want to use it—but my endurance/avionics bus supports more than 5 amps, so I am “considering” the Z-32 Heavy Duty E-Bus, which uses a relay. This made me think, if the alternate feed needs a relay, shouldn’t the main feed (avionics master switched) use a relay also? If not, why not? It’s doing the same thing normally that the alternate feed does if the main alternator fails—so why doesn’t it need a relay, too? But Bob’s recent post saying that relays are among the least reliable of components makes me nervous because in the combined schematic I am contemplating my Endurance Bus would be dependent on one relay in normal mode and two relays if I were operating in main-alternator-failed mode. Remember that the “Endurance Bus” used to be named the “Essential Bus” (for a legitimate reason). Should anything “Essential” really be totally dependent on relays? If not, I am looking for assistance in developing a better architecture that gives me a Heavy Duty (up to 8-amp) Essential/Avionics Bus with an avionics master switch.
Posted: Sat Sep 23, 2006 6:50 am Post subject: Eeeeek! Another fear and question. |
Well, I'll wait for Bob to justify his own
schematics, but I know he is in Kansas at the
tandem-wing fly-in today and may not be able to comment for a while.
If it were ME, I would not use a relay to power
the E-bus. I would use a switch. Switches
handle larger current than 5A all the time, and
if you're concerned about reliability, just use a
switch rated for larger current. The other thing
you should do here, since you're discovering you
have an unusual e-bus, is to ask yourself whether
all of those items really need to be on the
e-bus. I had to go through several iterations
before I finally pared my e-bus down to what was
really going to be necessary to have running ALL
THE TIME to complete the flight. Remember you
can always power up the Main Bus for a few
minutes if you need to, while on battery power.
Dave Morris
At 09:14 AM 9/23/2006, you wrote:
[quote]Well, I'm trying to understand the system I'm
<http://www.aeroelectric.com/Pictures/Schematics/E-BusFatFeed.gif>www.aeroelectric.com/Pictures/Schematics/E-BusFatFeed.gif
to use itbut my endurance/avionics bus supports
failsso why doesn’t it need a relay, too? But
nuckollsr(at)cox.net Guest
Posted: Sat Sep 23, 2006 7:08 am Post subject: Eeeeek! Another fear and question. |
Okay. That brings up a question. I m planning Z13/8 with Z32. Z32 Heavy
path. But Z13/8 also relies on a relay to supply the SD-8 s output to the
E-Bus. That s two relays that must work for E-Bus operations independent
This thread has expanded into a predictable level of
excitement for lack of perspective . . .
Note the key word in the quotation above . . . PRACTICAL
About 20 years ago, I was designing the first of a series
of electronically controlled rate controllers for
pitch trim on the Learjets. While conducting a Mil-HBK-217
MTBF study, it was interesting to note that when only
the electronic components, wires, solder joints and connectors
were factored into the study, MTBF for the device was in
the thousands of hours . . . about 7,000 as I recall.
When adding the last component, a mil-spec, 4-pole, double
throw, hermetically sealed 25A relay to the study, the predicted
MTBF fell to 900 hours for the system.
Mil-HBK-217 suggests and even accommodates de-rating of
parts to decrease stresses with commensurate increases in
MTBF. I was able to design the system so that the relay
was closed and bounce free before current flowed in the
contacts. Further, I was able to shut off all current flow
electronically before the relay contacts were opened.
Mil-HDK-217 had no prediction formula for my proposed scenario
but obviously, it was going to be as high as was PRACTICALLY
possible for incorporation of the relay. Twenty years later,
inquiries to the overhaul shop for this product tell me that
relays have NEVER been replaced in a unit returned for repair.
Even as I write these words, I'm designing the next new
product to appear in the AeroElectric Connection catalog
and the design incorporates a RELAY. Why not replace it
electronically? PRACTICALITY - it's technologically possible
but costs more . . . makes the product more expensive to
build and doesn't make it perform any better. It MIGHT
keep the system from needing maintenance attention before
the original owner sells the airplane . . . but I doubt
it.
The decision as to whether a relay or contactor is
PRACTICAL involves consideration of much more data than
the gross reliability factors. Cost of ownership and
FMEA for the SYSTEM figure heavily into the thought
process. We still use $25, el-cheeso contactors in our
airplanes because in spite of their need for periodic
maintenance, we have crafted a Plan-B to deal with those
failures. Hence my recommendation to many builders over
the years that 'upgrading' to Mil-Spec contactors in
their RV is dollars probably not well spent.
So before anyone goes of the end of the plank in
excitement or fear, know that suggestions for the
selection of ANY component need to be considered against
your ability to deal sweat-free with a failure of that
component. If your Plan-B is solid, then use of that
component is PRACTICAL and as free of excitement and
concerns as we know how to do.
Posted: Sat Sep 23, 2006 7:51 am Post subject: Eeeeek! Another fear and question. |
At 09:47 AM 9/23/2006 -0500, you wrote:
Well, I'll wait for Bob to justify his own schematics, but I know he is in
Kansas at the tandem-wing fly-in today and may not be able to comment for
a while.
If it were ME, I would not use a relay to power the E-bus. I would use a
switch. Switches handle larger current than 5A all the time, and if
you're concerned about reliability, just use a switch rated for larger
current. The other thing you should do here, since you're discovering you
have an unusual e-bus, is to ask yourself whether all of those items
really need to be on the e-bus. I had to go through several iterations
before I finally pared my e-bus down to what was really going to be
necessary to have running ALL THE TIME to complete the flight. Remember
you can always power up the Main Bus for a few minutes if you need to,
Dave Morris
The suggestion for adding an e-bus relay had nothing to do
with current carrying capacity of the e-bus switch. There's
be a long standing tradition in TC aircraft to limit the size
of always-hot feeders in aircraft to those protected by 5A or
smaller breakers.
Since the "FAT" e-bus feeder needs to carry more than the few
amps originally considered when the e-bus was conceived, the
idea for adding a 'mini-contactor' at the e-bus for larger
feeders was offered.
Now, fuses are much faster than breakers, and for Z-13/8
were a continuous e-bus load of 8A is PRACTICAL, then
assuming the e-bus alternate feed is fuse-fed from the
battery bus, going up to 10A fuse is a useful thing to
consider without thumbing our noses too vigorously at tradition.
Too many folks are treating the Z-figures as carved-in-
stone recommendations for details of a proposed electrical
system. These drawings are STARTING POINTS that illustrate
architectures that will in-turn drive your Plan-A/Plan-B
thinking.
Don't get yourselves wrapped around any axles here based
on sizes of wires, sizes of fuses/breakers or which
devices are fed from which busses. The drawings were
never intended to be a recipe for success, only a tool
for development. I get a half-dozen requests a week for
"Gee Bob, I like Figure Z-x but it doesn't . . . and
I want to . . . Would you please craft me a Z-y that
takes care of all my desires/worries?"
All these requests get the same reply which is not
much different that what I've written above. Nobody
promised anyone a decision free solution. One is
always on firm footing to clone the system out of
a C-172 and drive on. Any variations from that theme
WILL require thought, exploration, crafting/answering
of questions and finally understanding of the final
configuration which WILL be uniquely applicable to
YOU and your airplane.
Posted: Sat Sep 23, 2006 7:48 pm Post subject: Eeeeek! Another fear and question. |
Okay -- I think I get it.
First, I forgot the chief reason to use a relay in the first place -- to
keep fat wires short and if possible, out of the cockpit.
Second, I lost sight of the over-arching fact that just HAVING a back-up
alternator on board is a huge leap in reliability, not to mention STILL
having the last ditch option of keeping the lights on with the battery for a
couple of hours. < (smiley face with dunce cap)
I think the simple answer to my specific question is YES, use a relay in the
H.D. E-Bus normal feed line if that's the only way to keep the run from the
Main Bus to the switch and from the switch to the E-Bus under 6 inches or
so.
It is useful to know, however, that the relays might have a service life
short enough to consider replacing them at, say 500-hour intervals. Mine
will be living in a pretty benign environment, two of them just fwd of the
panel, and two just aft of the firewall.
In any conglomeration of components, it's a truism that one of them will be
the weakest link. Upgrade or eliminate it, and something else will
automatically become the weakest link. Although 900 hours MTBF seems pretty
short -- any ONE relay failing during a given flight will not produce a
life-threatening emergency in my plane. And I can carry a spare, as Bob
suggests in AEC.
Thanks Bob.
khurst(at)taroom.qld.gov. Guest
Posted: Sun Sep 24, 2006 6:48 pm Post subject: Eeeeek! Another fear and question. |
You said :
| Quote: | I was able to design the system so that the relay
You have me with my thinking cap on now ! If the current didn't flow
before the contacts were closed and was shut off before the contacts
opened, what was the purpose in having a relay ? It seems you had
complete control over the current flow without the relay !! Just
wondering ??
Kingsley in Oz.
Posted: Mon Sep 25, 2006 4:47 am Post subject: Eeeeek! Another fear and question. |
At 12:48 PM 9/25/2006 +1000, you wrote:
<khurst(at)taroom.qld.gov.au>
wondering ??
I was wondering if someone would pick up on that. You
get the prize.
When you hook motors to things that control flight
surfaces, you need to craft a fail passive architecture.
In this case, the electronics were a necessary component
of accurate control of pitch trim rate. There's
a fat transistor in series with the motor that takes
intelligence from other electronics to modulate supply
current as needed to maintain the required speed.
Obviously, the same transistor can turn the motor OFF
as well. I.e., all solid state control. However, several
failure modes would cause the fat transistor to stay ON
continuously causing a pitch trim runaway. We needed
a SECONDARY means for disconnecting pitch trim power
and the lowly relay seemed a good candidate due to its
very low on-resistance.
So, the relay was added but programmed via electronics
to close first and open last thereby offering VERY
long life contacts. However, monitor circuitry that
watches for a "stuck" fat transistor would also open
the relay, break power to the motor and illuminate a warning
light.
Last time I talked to the guys in overhaul, they'd seen
only one failure in the total fleet of Lears that might
have caused a pitch trim runaway wherein the monitor was
called upon to do its job. Interestingly enough, there's
a fair number of items returned for repair . . . virtually
all needed refurbishment of connection technologies. This
device is located high in the vertical fin of the airplane
. . . second worst environment in the airplane (hell hole
is #1). Products of corrosion and temperature cycles
have proven to be the biggest test of our design. The
stuff everyone worries about the most (electronics) have
proven quite robust and long lived.
frank.hinde(at)hp.com Guest
Posted: Mon Sep 25, 2006 9:14 am Post subject: Eeeeek! Another fear and question. |
Replace alt feed relay with a switch.
The SD8 relay is one of those things that is a second order failure...at least it is assuming you are using the SD8 as a backup to your main alternator....In other words the chances of the relay failing as well as the main alternator failing is extremly small.
Of course it means you need to test your SD8 operation regularly.....And you really DON't want to turn off your main alt with the engine running.
Frank
From: owner-aeroelectric-list-server(at)matronics.com [mailto:owner-aeroelectric-list-server(at)matronics.com] On Behalf Of John Swartout
Sent: Friday, September 22, 2006 2:43 PM
Subject: Eeeeek! Another fear and question.
wgill10(at)comcast.net Guest
Posted: Mon Sep 25, 2006 9:42 am Post subject: Eeeeek! Another fear and question. |
What harm is there in turning off the alternator (open the field) with the engine running?
[quote]-------------- Original message --------------
From: "Hinde, Frank George (Corvallis)" <frank.hinde(at)hp.com>
(at)font-face { font-family: Georgia; } (at)page Section1 {size: 8.5in 11.0in; margin: 1.0in 1.0in 1.0in 1.0in; } P.MsoNormal { FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman" } LI.MsoNormal { FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman" } DIV.MsoNormal { FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman" } A:link { COLOR: blue; TEXT-DECORATION: underline } SPAN.MsoHyperlink { COLOR: blue; TEXT-DECORATION: underline } A:visited { COLOR: purple; TEXT-DECORATION: underline } SPAN.MsoHyperlinkFollowed { COLOR: purple; TEXT-DECORATION: underline } SPAN.EmailStyle17 { FONT-WEIGHT: normal; COLOR: windowtext; FONT-STYLE: normal; FONT-FAMILY: Georgia } DIV.Section1 { page: Section1 } Replace alt feed relay with a switch.
Frank
| [b]
Posted: Mon Sep 25, 2006 10:23 am Post subject: Eeeeek! Another fear and question. |
At 05:39 PM 9/25/2006 +0000, you wrote:
| Quote: | What harm is there in turning off the alternator (open the field) with the
engine running?
IF . . . IF you're opening the field . . . no harm whatsoever.
On all TC aircraft, one may turn the alternator ON and OFF at
will under any conditions without risk to hardware.
Aircraft adaptations of internally regulated alternators pose
some risk of damage to the alternator's built in regulator due
to load dump if the b-lead is disconnected while the alternator
is under load.
Now, if the battery is fully charged -AND- all electro-whizzies
are OFF, the alternator is not significantly loaded and breaking
the b-lead a la Z-24 is low risk. So it's not so much a matter of
whether or not the alternator is being spun but a matter of
loads on the alternator at b-lead disconnect time.
Posted: Mon Sep 25, 2006 10:27 am Post subject: Eeeeek! Another fear and question. |
At 12:13 PM 9/25/2006 -0500, you wrote:
| Quote: | Replace alt feed relay with a switch.
The relay was added to facilitate OV protection . . .
Right. Probability of dual failures on any give tank
of fuel is exceedingly small.
Yup, preflight testing of all on-board energy sources is
a good idea. Most aircraft adaptations of automotive
alternators (internally regulated) cannot be turned off
once they've been turned on. This makes it difficult to
test an SD-8 except to make it the FIRST alternator you
turn on at preflight, then OFF, then turn the main alternator
ON.
If you're main alternator is an externally regulated device,
then it may be turned ON and OFF at will under any conditions
for any purpose.
Posted: Mon Sep 25, 2006 11:17 pm Post subject: Eeeeek! Another fear and question. |
| Quote: | > I was able to design the system so that the relay
wondering ??
Thank you for the explanation, I would never have worked it out myself.
Much obliged
Kingsley