A 3 phase AC (Alternating Current) question
PostPosted: Sun Feb 14, 2021 1:26 pm    Post subject: A 3 phase AC (Alternating Current) question Reply with quote
At 02:00 PM 2/14/2021, you wrote:
--> AeroElectric-List message posted by: "donjohnston" <don(at)velocity-xl.com>
Looking for some solutions on a project.
I have a lathe/mill combo. I'm going to be upgrading it by replacing the motors and controlling them with VFD's. Space is tight and it occurred to me that if I could use one VFD to control the motors (never at the same time) that would simplify the installation. It would also save money since I would only need one VFD. Very Happy
But now the question is how to switch the VFD between the two motors?
My first thought was a 3P2T switch. But I have not been able to find one rated for 230VAC and 1HP. It was suggested to use a contactor. But then I would need a low voltage source for the contactor with a switch for that power source and now it's no longer simplifying things.
How often do you switch? Perhaps a simple
drop-cord off each motor with a twist-lock
plug could be used to mate the in-service
motor with its power source.
out of that stuff?"
donjohnston
PostPosted: Sun Feb 14, 2021 2:02 pm    Post subject: Re: A 3 phase AC (Alternating Current) question Reply with quote
Unfortunately, often enough that I'd rather not be swapping cables. That's just as bad as having to move the belts to change speeds.
PostPosted: Sun Feb 14, 2021 2:09 pm    Post subject: A 3 phase AC (Alternating Current) question Reply with quote
Okay, then use a 2PDT switch or relay to switch
two of the three leads between motors. Leave the
3rd wire always connected between VFD and both
motors.
No current can flow to the 'unpowered' motor unless
at least TWO wires are connected. So leaving the
third wire always connected will have no effect
on system operations.
out of that stuff?"
PostPosted: Sun Feb 14, 2021 2:19 pm    Post subject: A 3 phase AC (Alternating Current) question Reply with quote
Plan C:
Use two of these puppies https://tinyurl.com/y2dya9lc
to effect your 2PDT switching. Only one contactor
energized at a time.
Then you can switch between motors with an itty-bitty
toggle switch located remotely from the high-voltage-fat-
wires.
You'll also need a 24vac source to power the
contactor coils
https://tinyurl.com/yytcqyuy
out of that stuff?"
PostPosted: Sun Feb 14, 2021 9:52 pm    Post subject: A 3 phase AC (Alternating Current) question Reply with quote
Would I use one leg of the 230v supply to power the coil?
(I haven't used a relay like this before)
See attached . . .
out of that stuff?"
MOTOR_SELECTOR_CKT_FOR_VFD.pdf
 Filename:  MOTOR_SELECTOR_CKT_FOR_VFD.pdf
 Filesize:  30.76 KB
 Downloaded:  491 Time(s)